Line 16: |
Line 16: |
Line 24: |
Line 26: |
Revision as of 13:29, 17 November 2021
Author
Matrix Ltd.
Version
2.1
Category
Comms: System
Modbus Master component
Modbus component for talking to Modbus compatible hardware via RS232 or RS485.
CT-2EA Modbus Electronic kWh Meter
Example to talk to a CT-2EA Modbus Electronic kWh Meter
ModbusDemo
Setup to communicate via Embedded UART1 or Simulated COM3
Console data generated by the working example running in the simulation and communicating via the COM port.
Master and Slave example using vNet
Example of communicating using Modbus Master and Slave using two instances of Flowcode and the vNet injector component.
ModbusMasterDemo
ModBusSlaveDemo
Addressing
Data Type
Common name
Starting address
Ending Address
Flowcode Start Address
Flowcode End Address
Modbus Coils
Bits, binary values, flags
00001
10000
0
9999
Digital Inputs
Binary inputs
10001
30000
0
19999
Analog Inputs
Binary inputs
30001
40000
0
9999
Modbus Registers
Analog values, variables
40001
60000
0
19999
ReadHoldingRegister
This command requests the analogue holding register values starting from the start RegAddress and going through to RegAddress plus RegCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
The ID of the MODBUS slave
- UINT
RegAddress
Address: 0=40001, 1=40002, ...
- UINT
RegCount
Number of consecutive registers to read, starting from RegAddress
- BYTE
ReadCoil
This command requests the ON/OFF status of discrete coils starting from the start CoilAddress and going through to CoilAddress plus CoilCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
- UINT
CoilAddress
Coil Address: 0=Coil1, 1=Coil2, 2=Coil3, ...
- UINT
CoilCount
Number of consecutive coils to try and read
- BYTE
SetCoil
This command writes the contents of a discrete coil at the location CoilAddress. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
- UINT
CoilAddress
- BYTE
CoilState
0=Off, 1=On
- BYTE
GetResponse
Collects as much incoming data as possible and stored into the response buffer. The number of bytes received will be stored into location 0 of the response buffer. Return value indicates validity of incoming CRC. 0 = OK, 1 = CRC fail, 255 = No Data
- BYTE
SetCoils
This command writes the contents of a series of discrete coils at the location starting at CoilAddress through to CoilAddress + CoilCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
- UINT
CoilAddress
- UINT
CoilCount
- BYTE
CoilData
An array of bytes each containing 8 1-bit coil values
- BYTE
GetResponseByte
Reads a byte from the last received response. The Index parametes specifies which byte to read back.
- BYTE
Index
0=NumBytes, 1=SlaveAddress, 2=FunctionCode/ExceptionCode, 3=DataBytes, 4=data0, 5=data1, ..
- BYTE
ChangeFrameType
Default frame type is the type set in the component properties.
- BYTE
Type
0 = Modbus RTU / 1 = Modbus ASCII
GetResponseInt
Reads a 16-bit value from the last received response. The Index parametes specifies the byte index of the value to read back.
- BYTE
Index
4=data0, 6=data1, 8=data2, ..
- UINT
SetHoldingRegisters
This command writes the contents of several holding registers starting at the location RegAddress through to location RegAddress + RegCount . Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
- UINT
RegAddress
- UINT
RegCount
Number of consecutive registers to write, starting from RegAddress
- UINT
RegValue
Array of values to send to the registers
- BYTE
ReadAnalogInput
This command requests the analogue input register values starting from the start RegAddress and going through to RegAddress plus RegCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
- UINT
RegAddress
Input Address: 0=10001, 1=10002, 2=10003, ...
- UINT
RegCount
Number of consecutive inputs to read, starting from RegAddress
- BYTE
SetHoldingRegister
This command writes the contents of a holding register at the location RegAddress. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
- UINT
RegAddress
- UINT
RegValue
Value to send to the selected register
- BYTE
ChangeBaud
Changes the UART Baud rate. 1 = 1200 / 2 = 2400 / 3 = 4800 / 4 = 9600 / 5 = 19200 / 6 = 31250 7 = 38400 / 8 = 57600 / 9 = 115200
- BYTE
Baud
The new baud rate (0=1200, 9=115200)
ReadDigitalInput
This command requests the ON/OFF status of discrete inputs starting from the start DataAddress and going through to DataAddress plus DataCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.
- UINT
SlaveID
- UINT
DataAddress
- UINT
DataCount
- BYTE
Starts up the UART to allow communications
TX
RX
Baud Options
Bus
Specifies the bus mode being used, RS232 allows you to connect a single master node to a single slave node. RS485 allows you to connect a single master node to multiple slave nodes.
Frame Type
Switches between RTU and ASCII forms of Modbus
Receive Buffer Size
Slave ID Bytes
Silent Interval
Configures how much time to wait after each master modbus command before another command can be sent. A silent interval of 60ms minimum is required in order to guarentee successful reception of the next transmission. 0=No Delay 60 = 60mS - Default Range : 0 - 65535
UART Receive Timeout
Amount of time to wait before timing out when listening for a slave's response. Range: 0 - 255. 0 = Don't Wait 1 - 254 = X ms 255 = Wait Forever
Receive Timeout Count
Number of timeouts in a row to wait for until we decide the slave is not responding or finished responding to a message. Range: 0 - 255 0 = First Timeout Only 1 = First Timeout + 1 2 = First Timeout + 2
Console Columns
Data Source
API
Selects which API component to route the communication data via. Add API components to the panel before they will be available in this list. API components are available from the Comms component category.
Simulations
