Modbus component for talking to Modbus compatible hardware via RS232 or RS485.
===<span style="font-weight: normal;"><u><tt>ReadHoldingRegister</tt></u></span>===
This command requests the analogue holding register values starting from the start RegAddress and going through to RegAddress plus RegCount.
Returns 0 for success, 1 for CRC fail and 255 for no reply.
'''Parameters'''
:[[Variable Types|UINT]] ''SlaveID''
::The ID of the MODBUS slave
:[[Variable Types|UINT]] ''RegAddress''
::Address: 0=40001, 1=40002, ...
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ReadHoldingRegister'''
| colspan="2" | This command requests the analogue holding register values starting from the start RegAddress and going through to RegAddress plus RegCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| width="90%" | SlaveID
| colspan="2" | The ID of the MODBUS slave&nbsp;
| width="90%" | RegAddress
| colspan="2" | Address: 0=40001, 1=40002, ...&nbsp;
| width="90%" | RegCount
| colspan="2" | Number of consecutive registers to read, starting from RegAddress&nbsp;
:[[Variable Types|UINT]] ''RegCount''
::Number of consecutive registers to read, starting from RegAddress
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ReadCoil'''
| colspan="2" | This command requests the ON/OFF status of discrete coils starting from the start CoilAddress and going through to CoilAddress plus CoilCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| width="90%" | CoilAddress
| colspan="2" | Coil Address: 0=Coil1, 1=Coil2, 2=Coil3, ...&nbsp;
| width="90%" | CoilCount
| colspan="2" | Number of consecutive coils to try and read&nbsp;
'''Return value'''
:[[Variable Types|BYTE]]
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''SetCoil'''
| colspan="2" | This command writes the contents of a discrete coil at the location CoilAddress. Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| width="90%" | CoilState
| colspan="2" | 0=Off, 1=On&nbsp;
===<span style="font-weight: normal;"><u><tt>ForceMultipleCoils</tt></u></span>===
This command writes the contents of a series of discrete coils at the location starting at CoilAddress through to CoilAddress + CoilCount.
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''GetResponse'''
| colspan="2" | Collects as much incoming data as possible and stored into the response buffer. The number of bytes received will be stored into location 0 of the response buffer. Return value indicates validity of incoming CRC. 0 = OK, 1 = CRC fail, 255 = No Data&nbsp;
'''Parameters'''
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''SetCoils'''
| colspan="2" | This command writes the contents of a series of discrete coils at the location starting at CoilAddress through to CoilAddress + CoilCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| width="90%" | CoilData
| colspan="2" | An array of bytes each containing 8 1-bit coil values&nbsp;
:[[Variable Types|UINT]] ''CoilAddress''
::Coil Address: 0=Coil1, 1=Coil2, 2=Coil3, ...
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''GetResponseByte'''
| colspan="2" | Reads a byte from the last received response. The Index parametes specifies which byte to read back. &nbsp;
| width="90%" | Index
| colspan="2" | 0=NumBytes, 1=SlaveAddress, 2=FunctionCode/ExceptionCode, 3=DataBytes, 4=data0, 5=data1, ..&nbsp;
:[[Variable Types|UINT]] ''CoilCount''
::Number of consecutive coils to try and read
:[[Variable Types|BYTE]] ''CoilData''
::An array of bytes each containing 8 1-bit coil values
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ChangeFrameType'''
| colspan="2" | Default frame type is the type set in the component properties.&nbsp;
| width="90%" | Type
| colspan="2" | 0 = Modbus RTU / 1 = Modbus ASCII&nbsp;
'''Return value'''
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''GetResponseInt'''
| colspan="2" | Reads a 16-bit value from the last received response.  The Index parametes specifies the byte index of the value to read back. &nbsp;
| width="90%" | Index
| colspan="2" | 4=data0, 6=data1, 8=data2, ..&nbsp;
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''SetHoldingRegisters'''
| colspan="2" | This command writes the contents of several holding registers starting at the location RegAddress through to location RegAddress + RegCount . Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| colspan="2" | Number of consecutive registers to write, starting from RegAddress&nbsp;
| width="90%" | RegValue
| colspan="2" | Array of values to send to the registers&nbsp;
===<span style="font-weight: normal;"><u><tt>ForceSingleCoil</tt></u></span>===
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ReadAnalogInput'''
| colspan="2" | This command requests the analogue input register values starting from the start RegAddress and going through to RegAddress plus RegCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| colspan="2" | Input Address: 0=10001, 1=10002, 2=10003, ...&nbsp;
| colspan="2" | Number of consecutive inputs to read, starting from RegAddress&nbsp;
'''Parameters'''
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''SetHoldingRegister'''
| colspan="2" | This command writes the contents of a holding register at the location RegAddress. Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| colspan="2" | Value to send to the selected register&nbsp;
:[[Variable Types|BYTE]] ''CoilState''
::0=Off, 1=On
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ReadDigitalInput'''
| colspan="2" | This command requests the ON/OFF status of discrete inputs starting from the start DataAddress and going through to DataAddress plus DataCount. Returns 0 for success, 1 for CRC fail and 255 for no reply.&nbsp;
| width="90%" | DataAddress
| width="90%" | DataCount
'''Return value'''
| colspan="2" | Starts up the UART to allow communications&nbsp;
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ReadByteFromBuffer'''
| colspan="2" | Reads a byte of data from the local sector buffer. Return = Data byte read from the local sector buffer. &nbsp;
| width="90%" | Address
| colspan="2" | 0 - 511 - Contains the position of the byte to be read&nbsp;
===<span style="font-weight: normal;"><u><tt>GetResponse</tt></u></span>===
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ReadFileLength'''
| colspan="2" | Returns the number of bytes in the current sector that are used by the current open file. Return = 512 - Sector is filled with file data Return < 512 - Last sector of the file, Retval specifies how many bytes of data are remaining in the sector&nbsp;
'''Parameters'''
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''OpenFile'''
| colspan="2" | Searches for and opens a file for reading or writing from within the current directory on the disk. Returns 0 for success.&nbsp;
| width="90%" | Filename
| colspan="2" | 8.3 filename of the file we are trying to open e.g. "file.txt"&nbsp;
'''Return value'''
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''WriteFileSector'''
| colspan="2" | Overwrites the current sector on the memory card with the contents of the local sector buffer. See write_byte_to_buffer function. Return = 0 - File sector written successfully. Return > 0 - File sector write error&nbsp;
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''SetFileIndex'''
| colspan="2" | Sets the current file index and used to switch between several open file streams.  Default = 0. &nbsp;
| width="90%" | File_Index
| colspan="2" | File index ranges from 0 to (Max Concurrent Files - 1)&nbsp;
===<span style="font-weight: normal;"><u><tt>ReadCoilStatus</tt></u></span>===
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''AppendStringToFile'''
| colspan="2" | Adds the contents of the data string parameter to the end of the currently open file. Returns 0 for success.&nbsp;
| width="90%" | Data_String
| colspan="2" | Data to append to the end of the file&nbsp;
'''Parameters'''
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''ReadFileSize'''
| colspan="2" | Reads the entire size of the current file in bytes.&nbsp;
| width="10%" align="center" style="border-top: 2px solid #000;" | [[File:Fc9-u32-icon.png]] - ULONG
| width="90%" style="background-color:#D8C9D8; color:#4B008D;" | '''SetTimeAndDate'''
| colspan="2" | Sets the current time and date.  Time = (Hour << 11) + (Min << 5) + (Sec >> 1) Date = (YearFrom1980 << 9) + (Month << 5) + (Day) Additional details can be found here: http://www.maverick-os.dk/FileSystemFormats/FAT16_FileSystem.html#TimeFormat&nbsp;
| width="90%" | Time
| colspan="2" | Sets the current Time in FAT Time format hhhhhmmmmmmsssss - S=Secs/2&nbsp;
| width="90%" | Date
| colspan="2" | Sets the current Date in FAT Date format yyyyyyymmmmddddd - Y=Years since 1980&nbsp;
'''Return value'''
===<span style="font-weight: normal;"><u><tt>GetResponseByte</tt></u></span>===
| colspan="2" | Attempts to communicate with the SD card and if successful sets up the file system. Returns 0 for success. &nbsp;
'''Parameters'''
:[[Variable Types|BYTE]] ''Index''
::0=NumBytes, 1=SlaveAddress, 2=FunctionCode/ExceptionCode, .....
'''Return value'''
===<span style="font-weight: normal;"><u><tt>ReadInputStatus</tt></u></span>===
'''Parameters'''
:[[Variable Types|UINT]] ''DataAddress''
::Input Address: 0=10001, 1=10002, 2=10003, ...
:[[Variable Types|UINT]] ''DataCount''
::Number of consecutive inputs to read, starting from RegAddress
'''Return value'''
===<span style="font-weight: normal;"><u><tt>ChangeFrameType</tt></u></span>===
'''Parameters'''
:[[Variable Types|BYTE]] ''Type''
::0 = Modbus RTU / 1 = Modbus ASCII
'''Return value'''
===<span style="font-weight: normal;"><u><tt>PresetSingleRegister</tt></u></span>===
This command writes the contents of a analogue output holding registerl at the location RegAddress.
'''Parameters'''
:[[Variable Types|UINT]] ''RegValue''
::Value to send to the selected register
'''Return value'''
===<span style="font-weight: normal;"><u><tt>GetResponseInt</tt></u></span>===
'''Parameters'''
'''Return value'''
===<span style="font-weight: normal;"><u><tt>ReadInputRegister</tt></u></span>===
'''Parameters'''
'''Return value'''
===<span style="font-weight: normal;"><u><tt>PresetMultipleRegisters</tt></u></span>===
This command writes the contents of several analogue output holding registers starting at the location RegAddress through to location RegAddress + RegCount .
'''Parameters'''
::Number of consecutive registers to write, starting from RegAddress
::Array of values to send to the registers
'''Return value'''
'''Parameters'''
'''Return value'''
| colspan="2" | Initialise the comms to the Arduino board ready for commands to be sent.&nbsp;
==Property reference==
<span style="font-weight: normal;"><u>Frame Type</u></span>
This property is of type ''Fixed list of ints'' and can be referenced with the variable name ''FrameType''.
Switches between RTU and ASCII forms of Modbus
<span style="font-weight: normal;"><u>Receive Buffer Size</u></span>
This property is of type ''Unsigned integer'' and can be referenced with the variable name ''ReceiveBufferSize''.
| width="90%" | Frame Type
| colspan="2" | Switches between RTU and ASCII forms of Modbus&nbsp;
<span style="font-weight: normal;"><u>Slave ID Bytes</u></span>
This property is of type ''Unsigned integer'' and can be referenced with the variable name ''AddressBytes''.
| width="90%" | Receive Buffer Size
| colspan="2" | Maximum number of bytes the receive buffer can hold&nbsp;
<span style="font-weight: normal;"><u>Silent Interval</u></span>
| width="90%" | Slave ID Bytes
This property is of type ''Unsigned integer'' and can be referenced with the variable name ''SilentInterval''.
| colspan="2" | Number of bytes used when passing a slave ID, usually 1 but sometimes 2&nbsp;
Configures how much time to wait after each master modbus command before another command can be sent.
A silent interval of 60ms minimum is required in order to guarentee successful reception of the next transmission.
| width="90%" | Silent Interval
0=No Delay
| colspan="2" | Configures how much time to wait after each master modbus command before another command can be sent. A silent interval of 60ms minimum is required in order to guarentee successful reception of the next transmission. 0=No Delay 60 = 60mS - Default Range : 0 - 65535&nbsp;
60 = 60mS - Default
| width="90%" | UART Receive Timeout
Range : 0 - 65535
| colspan="2" | Amount of time to wait before timing out when listening for a slave's response. Range: 0 - 255. 0 = Don't Wait 1 - 254 = X ms 255 = Wait Forever&nbsp;
<span style="font-weight: normal;"><u>UART Receive Timeout</u></span>
This property is of type ''Unsigned integer'' and can be referenced with the variable name ''RXTOUT''.
| width="90%" | Receive Timeout Count
| colspan="2" | Number of timeouts in a row to wait for until we decide the slave is not responding or finished responding to a message. Range: 0 - 255 0 = First Timeout Only 1 = First Timeout + 1 2 = First Timeout + 2&nbsp;
Range: 0 - 255.
| width="90%" | Label
0 = Don't Wait
| colspan="2" | A text label to appear on the Modbus panel object.&nbsp;
1 - 254 = X ms
255 = Wait Forever
| width="90%" | Console Data
<span style="font-weight: normal;"><u>Receive Timeout Count</u></span>
| colspan="2" | Selects if the console data is automatically generated or not&nbsp;
This property is of type ''Unsigned integer'' and can be referenced with the variable name ''TOUTCNT''.
| width="90%" | Console Columns
| colspan="2" | Number of characters that can be displayed on a single line of the console.&nbsp;
to a message.
Range: 0 - 255
| width="90%" | Data Source
| colspan="2" | Simulation data source used to allow the component to connect to various remote devices    Nothing - Simulation data is ignored    COM port - Routes the communication data to and from a physical or virtual COM port     Injector - Routes the communication data via a data injector component on the Panel.&nbsp;
| width="90%" | COM Port
| colspan="2" | Lists all the current available COM port hardware on your PC.&nbsp;
<span style="font-weight: normal;"><u>Label</u></span>
This property is of type ''Line of text'' and can be referenced with the variable name ''label''.
| width="90%" | Refresh Ports
| colspan="2" | &nbsp;
<span style="font-weight: normal;"><u>Console Data</u></span>
| width="90%" | Baud Rate
This property is of type ''True or false'' and can be referenced with the variable name ''scada_uart1::ConsoleData''.
| colspan="2" | COM port data rate in bits per second&nbsp;
<span style="font-weight: normal;"><u>Console Columns</u></span>
This property is of type ''Unsigned integer'' and can be referenced with the variable name ''scada_uart1::ConsoleColumns''.
<span style="font-weight: normal;"><u>Data Source</u></span>
This property is of type ''Fixed list of ints'' and can be referenced with the variable name ''scada_uart1::DataSource''.
<span style="font-weight: normal;"><u>COM Port</u></span>
This property is of type ''Fixed list of ints'' and can be referenced with the variable name ''scada_uart1::com_port''.
<span style="font-weight: normal;"><u>Baud Rate</u></span>
This property is of type ''Unsigned integer'' and can be referenced with the variable name ''scada_uart1::baud''.
Revision as of 20:43, 16 November 2021
Version 2.1
Category Comms: System
Fc9-comp-macro.png ReadHoldingRegister
Fc9-u16-icon.png - UINT SlaveID
Fc9-u16-icon.png - UINT RegAddress
Fc9-u16-icon.png - UINT RegCount
Fc9-comp-macro.png ReadCoil
Fc9-u16-icon.png - UINT CoilAddress
Fc9-u16-icon.png - UINT CoilCount
Fc9-comp-macro.png SetCoil
Fc9-u8-icon.png - BYTE CoilState
0=Off, 1=On
Fc9-comp-macro.png GetResponse
Fc9-comp-macro.png SetCoils
Fc9-u8-icon.png - BYTE CoilData
Fc9-comp-macro.png GetResponseByte
Fc9-u8-icon.png - BYTE Index
Fc9-comp-macro.png ChangeFrameType
Fc9-u8-icon.png - BYTE Type
Fc9-comp-macro.png GetResponseInt
Fc9-comp-macro.png SetHoldingRegisters
Fc9-u16-icon.png - UINT RegValue
Fc9-comp-macro.png ReadAnalogInput
Fc9-comp-macro.png ReadDigitalInput
Fc9-u16-icon.png - UINT DataAddress
Fc9-u16-icon.png - UINT DataCount
Fc9-comp-macro.png Initialise
Fc9-comp-macro.png ReadByteFromBuffer
Fc9-u16-icon.png - UINT Address
Fc9-comp-macro.png ReadFileLength
[[File:]] - Return
Fc9-comp-macro.png OpenFile
Fc9-comp-macro.png WriteFileSector
Fc9-comp-macro.png SetFileIndex
Fc9-u8-icon.png - BYTE File_Index
Fc9-comp-macro.png AppendStringToFile
Fc9-string-icon.png - STRING Data_String
Fc9-comp-macro.png ReadFileSize
Fc9-u32-icon.png - ULONG Return
Fc9-comp-macro.png SetTimeAndDate
Fc9-u16-icon.png - UINT Time
Fc9-u16-icon.png - UINT Date
Fc9-type-16-icon.png Frame Type
Fc9-type-21-icon.png Receive Buffer Size
Fc9-type-21-icon.png Slave ID Bytes
Fc9-type-21-icon.png Silent Interval
Fc9-type-21-icon.png UART Receive Timeout
Fc9-type-21-icon.png Receive Timeout Count
Fc9-type-10-icon.png Label
Fc9-type-21-icon.png Console Columns
Fc9-type-16-icon.png Data Source
Fc9-type-16-icon.png COM Port
Fc9-type-7-icon.png Refresh Ports
Fc9-type-21-icon.png Baud Rate
Fc9-conn-icon.png Simulations