Component: PID Control (DSP Operators): Difference between revisions
Line 234: Line 234:
| colspan="2" | Sets the buffer data type.
| width="90%" style="background-color:#EAE1EA; color:#4B008D;" | Control
| width="90%" class="mtx-class-propfolder" | Control
Line 268: Line 268:
| colspan="2" | Time in seconds between each sample
| width="90%" style="background-color:#EAE1EA; color:#4B008D;" | Integral Properties
| width="90%" class="mtx-class-propfolder" | Integral Properties
Line 287: Line 287:
| colspan="2" | Minimum value that the integral value can go to.
| width="90%" style="background-color:#EAE1EA; color:#4B008D;" | Derivative Properties
| width="90%" class="mtx-class-propfolder" | Derivative Properties
Version 1.2
Category DSP Operators
PID Control component
Control algorythm based on Proportional, Integral and Differential error. P/PI/PID - Mathematical control process to get to the setpoint as fast as possible, similar to the process in the human brain when steering a car. Used to accurately control things like motors, temperatures etc.
Please click here to download the component source project: FC_Comp_Source_DSP_PIDControl.fcfx
Please click here to view the component source code (Beta): FC_Comp_Source_DSP_PIDControl.fcfx
Setpoint = Value that the user wishes the system to be running at. e.g. the temperature control knob for an oven.
Feedback = Measurement to monitor the value we are controlling. e.g. the temperature reading inside the oven.
Control Signal = The value we want to output to the device. e.g. the signal sent to the heat element inside the oven.
Proportional (P) - Provides an instantaneous kick to try and get the control variable to the setpoint as quickly as possible. P control alone will generally always end up with some form of steady state error. If this is acceptable then P control alone is very easy to perform and stable as long as the P gain is not excessive.
Integral (I) - Provides an accumulation of error over time to try and minimise any steady state error. PI control alone can be a very suitable option for controlling a lot of systems. A potential problem with I control is if the control variable goes into saturation and cannot for whatever reason reach the setpoint. This can cause the I accumulator to get larger and larger and then if the saturation is removed the system can become very unstable. Integral clamping allows the integral accumulator to be held within a certain range and avoid excessive windup.
Derivative (D) - Provides a delaying effect when the error is changing fast. This can have the effect of dampening oscillations and allowing the P and I gains to be increased further to provide faster and more stable responses. The D term can be tricky to get right and too much especially when used with a noisy feedback signal can lead to instabilities. The D filter allows for some high frequency noise to be removed from the feedback.
Here is a project file showing an PID control system for a system such as an high accuracy temperature controller e.g. a 3D printer hotend.
The setpoint is set via an analogue input which controls the desired temperature of the system.
In this first example the feedback is provided using the simulated load DSP component which simply takes a percentage of the last output and combines with a percentage of the new output.
This allows easy moddeling of systems such as devices that heat up and cool down over time which allows you to see the system in action.
You assign a setpoint and then the system will get to temperature and then maintain the temperature by automatically adjusting the output duty.
PID Control Simulated Output Example
In this second example the feedback is provided via a temperature sensor component. This shows how you would do it with a real system using a sensor to complete the feedback loop.
PID Control Example
As with other DSP components the raw signals and values can be seen in the data recorder and console windows.
ChangePID
ChangePID
Allows the P, I and D control parameters to be changed on the fly during a program.
- FLOAT P
- FLOAT I
- FLOAT D
GetPIDPortions
GetPIDPortions
Collects a single contribution from the PID output.
- BYTE Index
0=P, 1=I, 2=D
- FLOAT Return
Process
Process
Processes the current value from a buffer.
ProcessArray
ProcessArray
Processes an entire buffer, either by performing the control operation to every value in the buffer or just the last value.
Setpoint Connect To
Feedback Connect To
Buffer Size
Buffer Type
Control
Method
Specifies which control method will be used to process the buffer data
Proportional Gain (K)
P coefficient used to perform the Proportional gain calculation.
Integration Time (Ti)
I coefficient used to perform the Integral calculation in relation to the sample time.
Derivative Time (Td)
D coefficient used to perform the Derivative calculation in relation to the sample time.
Invert Error
Some systems may require an inverted response. No = Error = Setpoint - Feedback Yes = Error = Feedback - Setpoint
Sample Time
Integral Properties
Integral Clamping
Used to prevent the negative effects of integral windup. Clamps the integral responce between the min and max values.
Clamping Max
Maximum value that the integral value can go to.
Clamping Min
Monitor Setpoint
Automatically monitors the setpoint allowing the derivative filter and old error to be cleared whenever the setpoint value changes.
Derivative Filtering
Allows the calculated derivative value to be filtered to improve the response and get rid of high frequency noise.
Filter Coefficient
Coefficient used to calculate the response of the filter, the higher the value the more filtering is performed